Transformers
Gerards Gavrilovs, Olegs Borscevskis
Riga Technical University
gerards.gavrilovs@latvenergo.lv, olegs.borscevskis@latvenergo.lv
I.
INTRODUCTION
II.
23
C. Moisture Content
Moisture, especially in presence of oxygen is extremely
hazardous to transformer insulation. Each time the moisture is
doubled in a transformer, the live of the insulation is cut by
one-half. The technical staff must keep in mind that the life of
the transformer is the life of the paper and the life of the
paper is extended by keeping out moisture and oxygen.
Oil should be dried when moisture in oil overachieve
values given in standard. Segregated technical decision is
possible too.
G. Interfacial Tension
As oil ages, it is contaminated by tiny particles (oxidation
products) of the oil and paper insulation. Particles on top of
the water extend across the water/oil interface line which
weakens the surface tension between the two liquids.
Particles in oil weaken interfacial tension and lower the
interfacial tension number. Interfacial tension and acid
number, Fig. 1, together are an excellent indication of when
oil needs to be reclaimed. It is recommended the oil be
reclaimed-filtered when the interfacial tension number falls to
25 dynes per centimeter.
E. Flash Point
The flash point and fire point refer to the flammability
characteristics of the fluid being tested. The flash point is
defined as the lowest temperature at which the vapor formed
above a pool of the liquid ignites in air at a pressure of one
atmosphere.
The flash point is used to assess the hazardous nature of a
material and the risk of the materials ability to support
combustion. A low flash point can be indicative of the
presence of highly volatile materials in the fluid. For mineral
oils the minimum accepted value for the flash point oil used
in outdoor transformers is 145oC, although this could vary
according to local standards. In general the fire points are
about 10oC higher than the flash point [3].
F. Acidity
The acidity of an oil sample is related to the deterioration
of the sample. The mineral oil insulating fluid is essential a
non-polar saturated hydrocarbon, however, when the sample
24
H. Particles Contamination
Particles of sludge materials can indicate the products of
oxidation such as acids that will raise the acidity and lower
the interfacial tension. Particles of carbon and metal can
indicate severe local overheating and or arcing. All of these
can suggest further testing to determine the source of these
materials and decide about necessity of oil treatment.
Particles may be drawn into or expelled from high stress
regions. Fine particles may agglomerate or be dispersed.
Particle chains may develop. These complex physical factors
have not been related directly to voltage breakdown in the oil.
Particles may cause partial discharges to develop in oil but
these discharges also have not been related directly to short
time breakdown of the oil. Insulating oil which is deteriorated
with particles has to get purification process.
III.
Oil parameters
Breakdown
voltage, kV
Dielectric losses,
%
Flash point, oC
Moisture content
in oil, ppm
Acidity,
mgKOH/g of oil
Particles,
according
ISO4406:2004
Color (visual)
Before oil
regeneration
After oil
regeneration
14
75
7.55
0.06
143
145
60.68
6.0
0.051
0.01
21/19/15
14/13/9
Brown (dark)
Clear, light
yellow
25
Oil
parameters
Breakdown
voltage, kV
Dielectric
losses, %
Flash point,
o
C
Moisture
content in oil,
ppm
Acidity,
mgKOH/g of
oil
Particles,
according
ISO4406:2004
IV.
2007
2008
2009
2010
73
73
71
67
1.0
1.72
1.64
1.8
143
143
143
139
8.75
12.05
12.5
9.32
0.01
0.01
0.01
0.013
15/12/9
15/13/9
15/13/10
15/13/10
26
REFERENCES
CONCLUSIONS
[1]
[2]
[3]
[4]
[5]
[6]
[7]
[8]
27
M. Fingas, The basics of oil spill cleanup, 2nd ed, Boca Raton, FL:
CRC Press; 2000.
M. Fingas, Oil spill science and technology, in Proc. Gulf
Professional Publishing, ISBN-13/ 9781856179430, 2011, pp.119
IEC 60085:2004, Electrical insulation. Thermal classification,
International Electrotechnical Commission, 2004, pp.12.
L.Berzina-Cimdina, V. Lakevics and A. Ruplis, Characterisation of
new sorbents produced from by-product of the rapeseed oil treatment,
Scientific Journal of RTU, ID4510, 2008.
EKOFLUID, Transformer oil regeneration technology, 2007.
Amish R.S, Condition Assessment Techniques for Large Power
Transformers, Curtin University of Technology, Karrinyup, Australia,
Tech. Rep., 09820207, Nov. 2005.
E. Figueroa, T. Kalicki and E. TeNyenhuis, Low frequency heating
field dry-out of a 750MVA 500kV autotransformer, Electricity Today,
2009
C. Sumereder, M, Muhr, Moisture determination and degradation of
solid insulation system of power transformers, in Proc. of 2010
Conference Record of IEEE International Symposium on Electrical
Insulation, art. No. 5549775