Discussion of Rules of Interlocking:

 What is portion of what is typically shown on Siemens Single Line for GIS Project

 Simplifying the Circuit for our discussion

o
 Overview of Power Delivery

```````

o Shown with Single Line notations for Circuit Breaker and Disconnect Switch – Ground not shown

````````

o Considering “Real World” – Disc Closed, CB Closed, No Grounds

o Considering Maintenance – CB Open First, then Disc Open, Grounds Applied


 Discussion of Specific Devices that are controlled in GIS System

Equipment Function Open / Close If (Most Cases)


Circuit Breaker Breaks Volt / Amp Load in Circuit Always able to Open
Disconnect Switch Breaks Voltage / Energized Line Open if Breaker is Open

Treated as “Maintenance” Points


Ground Switch Treated as “Safety” Points Close if Disconnect is Open

Unsafe to close if it will close into


an “energized” line
Fast Acting Ground Switch Treated as “Dissipation” Point Close if Disconnect is Open

Unsafe to close if it will close into


an “energized” line
 Discussion of a System showing Device Operation
o Typical Setup –
 The system is feeding power into a house
 CB Closed, Disc Closed, Grounds Open

o Forced Outage due to storm


 A tree falls onto the line near the house
 To break the “fault”, the CB will Automatically open after devices detect an interrupt in power flow
 CB Open, Disc Closed, Grounds Open

o Checking the System


 Once the tree is cleared, a utility crew will go to the substation to “close” the breaker back
 If there is no issue, the CB will close back
 HOWEVER, if needed, the crew will do maintenance on the CB
 To be safe, they will isolate the CB from the system in the following manner
 Open the Disconnect Switch to stop the flow of voltage
 Apply Ground Switch as a safety point. This further protects the crew in case the
Disconnect Switch closes by accident. The voltage would not flow into the CB, but force
the voltage into the “ground”
 CB Open, Disc Open, Grounds Closed

o Restoring System
 Once work is complete, the Grounds are removed First, then Disconnect Closed, then CB Closed
in the final step.